Calculation does not complete for unheated buildings

Modified on Mon, 21 Apr, 2025 at 4:11 PM

Related Articles:

Foundation Area and Maximum Number Of Storeys


Interfaces to SBEM v6 (including DesignBuilder v7) raise an error and do not complete the calculation for buildings which have no heated zones.



This is because SBEM checks that the model includes a non-zero setting for the Foundation Area (as defined in the 2021 NCM).



The Foundation Area calculation uses zone areas of zones which have an HVAC System assigned



DesignBuilder calculates the Foundation Area automatically.

So it will be calculated as zero for an unheated building.

SBEM checks to ensure that the Foundation Area is not zero during the calculation and stops it if that is the case

How to generate an XML for an Unheated Building

The EPC Conventions do not currently provide advice on generating an XML for unheated buildings for SBEM v6.

Some Accreditation Schemes are advising to set Foundation Area to 1m² (the minimum value accepted by SBEM) to unblock XML generation.

This is also our advice.

Note that the Foundation Area does not affect the EPC Rating, it is only used in deriving the Notional Building TER.

The TER is used in deriving the benchmarks 'Newly Built' and 'typical' which appear on the EPC.


You can manually set the Foundation Area in Project Details:


Note this is unlikely to have any significant effect on the Newly Built and Typical ratings, thus it should be safe to force the Foundation Area to 1m².

For example, for the location 'London' a Foundation Area of 1 m² will represent a reduction of 4.3 kg of CO2 emissions for the Notional Building classified as Side-Lit (eg office) and 8.6kg of CO2 if classified as Top-Lit (eg warehouse) (equivalent to a reduction of 0.043 or 0.086 in the TER for a building of area 100 m²). For larger buildings, the TER reduction will be less (0.0043 or 0.0086 for 1000 m²).

Example
For an Unheated warehouse of 400m² (with T8 lighting and gas DHW)-ie using Designbuilder defaults
    BER = 5.0438 kgCO2/m²
    SER (Reference Building) = 3.8369 kgCO2/m²
    Rating = 5.0438/3.8369*50 = 65.72 = 66


With a Foundation Area of 1m²
    TER = 1.07981 kgCO2/m²
    Newly Built rating = 1.07981 / 3.8369 * 50 = 14.07 =14
    Typical= 14.07 * 4 = 56.28 = 56

With a Foundation Area of 0m² (correct setting for Unheated Building)
    TER = 1.10129kgCO2/m²
    Newly Built rating = 1.10129 / 3.8369 * 50 =14.3 = 14
    Typical= 14.3513 * 4 =57.4 = 
57

Was this article helpful?

That’s Great!

Thank you for your feedback

Sorry! We couldn't be helpful

Thank you for your feedback

Let us know how can we improve this article!

Select at least one of the reasons
CAPTCHA verification is required.

Feedback sent

We appreciate your effort and will try to fix the article