The 2021 (England) & 2022 (Scotland and Wales) NCMs now offer a range of lighting illuminance for each activity (though in some cases the minimum and maximum values are identical). By default the minimum (also referred to as 'Standard') value is used. For over 50% of the NCM activities the 2021 minimum value does not match the previous default value and thus lighting consumption in Actual and Reference Buildings may be significantly different to earlier assessments.
Note you can check the Minimum and Maximum Illuminance for a specific activity by setting the specification to 'Design':

Note if the Design illuminance field is not set (ie left as zero), the standard (minimum) illuminance is used. You can set an illuminance outside these limits but if that is below the standard illuminance the lighting will be 'upgraded' to an equivalent efficiency based on an illuminance equal to the standard value.
The following tables list the current and previous default values. Increased and Decreased values are highlighted:
Offices / Workshop businesses
| Activity | 2021 | 2013 |
| Car Park | 75 | 100 |
| Office | 300 | 400 |
| Changing | 100 | 100 |
| Circulation | 100 | 100 |
| FoodPrep | 500 | 500 |
| Plant | 200 | 200 |
| Toilet | 200 | 200 |
| WkshpSS | 300 | 300 |
| EatDrink | 200 | 150 |
| Reception | 300 | 200 |
| Gym | 300 | 150 |
| Store | 100 | 50 |
Retail and Financial/Professional services
|
Hospitals and Care Homes
| Activity | 2021 | 2013 |
| Diagnostic | 50 | 1000 |
| Reception | 200 | 500 |
| OpTheatre | 500 | 1000 |
| PostMortem | 500 | 1000 |
| AEConsRm | 300 | 500 |
| Lecture | 200 | 300 |
| Store | 100 | 150 |
| Wards | 100 | 150 |
| Laund | 300 | 400 |
| Bed | 100 | 125 |
| Bed24x7 | 100 | 125 |
| Offices | 300 | 350 |
| Changing | 100 | 100 |
| Circulation | 100 | 100 |
| CirculationPub | 100 | 100 |
| ClassRm | 300 | 300 |
| Hydrotherapy | 300 | 300 |
| IndProcess | 300 | 300 |
| Physiotherapy | 300 | 300 |
| Toilet | 200 | 200 |
| Lab | 500 | 400 |
| Plant | 200 | 150 |
| Bath | 200 | 125 |
| EatDrink | 200 | 125 |
| FoodPrep | 500 | 300 |
Storage or Distribution
| Activity | 2021 | 2013 |
| 24x7WareStore | 100 | 300 |
| WareStore | 100 | 300 |
| Reception | 100 | 200 |
| 24x7Office | 300 | 400 |
| Office | 300 | 400 |
| Changing | 100 | 100 |
| Circulation | 100 | 100 |
| FoodPrep | 500 | 500 |
| Plant | 200 | 200 |
| Toilet | 200 | 200 |
| EatDrink | 200 | 150 |
| Store | 100 | 50 |
Hotels
| Activity | 2021 | 2013 |
| Office | 300 | 400 |
| Changing | 100 | 100 |
| Circulation | 100 | 100 |
| DrySptHall | 300 | 300 |
| Ensuite Bedroom | 100 | 100 |
| FoodPrep | 500 | 500 |
| Hall | 300 | 300 |
| Laund | 300 | 300 |
| Plant | 200 | 200 |
| Swim | 300 | 300 |
| Toilet | 200 | 200 |
| Bedroom | 100 | 80 |
| Bath | 200 | 150 |
| EatDrink | 200 | 150 |
| Reception | 300 | 200 |
| FitGym | 300 | 150 |
| Store | 100 | 50 |
Community/Day Centre
| Activity | 2021 | 2013 |
| Reception | 100 | 200 |
| WkshpSS | 300 | 500 |
| Lecture | 200 | 300 |
| Offices | 300 | 400 |
| Changing | 100 | 100 |
| Circulation | 100 | 100 |
| DrySptHall | 300 | 300 |
| FoodPrep | 500 | 500 |
| Plant | 200 | 200 |
| Toilet | 200 | 200 |
| EatDrink | 200 | 150 |
| Store | 100 | 50 |
Primary Health Care
| Activity | 2021 | 2013 |
| Offices | 300 | 445 |
| Circulation | 100 | 100 |
| Plant | 200 | 200 |
| Reception | 200 | 200 |
| Toilet | 200 | 200 |
| Store | 100 | 50 |
Non Residential Schools
| Activity | 2021 | 2013 |
| Toilet | 100 | 200 |
| Lab | 500 | 800 |
| Offices | 300 | 400 |
| Changing | 100 | 100 |
| Circulation | 100 | 100 |
| DrySptHall | 300 | 300 |
| FoodPrep | 500 | 500 |
| HighDensIT | 300 | 300 |
| Lecture | 300 | 300 |
| Plant | 200 | 200 |
| Swim | 300 | 300 |
| WkshpSS | 500 | 500 |
| Teaching | 300 | 280 |
| EatDrink | 200 | 150 |
| Reception | 300 | 200 |
| Store | 100 | 50 |
Residential schools
| Activity | 2021 | 2013 |
| Toilet | 100 | 200 |
| Lab | 500 | 800 |
| Offices | 300 | 400 |
| Bedroom | 100 | 125 |
| Changing | 100 | 100 |
| Circulation | 100 | 100 |
| DrySptHall | 300 | 300 |
| FoodPrep | 500 | 500 |
| HighDensIT | 300 | 300 |
| Laund | 300 | 300 |
| Lecture | 300 | 300 |
| Plant | 200 | 200 |
| Swim | 300 | 300 |
| WkshpSS | 500 | 500 |
| Teaching | 300 | 280 |
| Residents common rooms | 200 | 150 |
| EatDrink | 200 | 150 |
| Reception | 300 | 200 |
| Bathroom | 200 | 125 |
| Store | 100 | 50 |
Restaurant and Cafes/Drinking Establishments and Hot Food takeaways
| Activity | 2021 | 2013 |
| Stage | 300 | 750 |
| Office | 300 | 400 |
| Circulation | 100 | 100 |
| FoodPrep | 500 | 500 |
| Plant | 200 | 200 |
| Toilet | 200 | 200 |
| EatDrink | 200 | 150 |
| Store | 100 | 50 |
Libraries Museums and Galleries
| Activity | 2021 | 2013 |
| Reception | 100 | 200 |
| WkshpSS | 300 | 500 |
| Lab | 500 | 800 |
| Lecture | 200 | 300 |
| Offices | 300 | 400 |
| Circulation | 100 | 100 |
| FoodPrep | 500 | 500 |
| Plant | 200 | 200 |
| Toilet | 200 | 200 |
| EatDrink | 200 | 150 |
| Store | 100 | 50 |
General Assembly and Leisure plus Night Clubs and Theatres
| Activity | 2021 | 2013 |
| Stage | 300 | 750 |
| CirculationPub | 100 | 200 |
| Reception | 100 | 200 |
| Sales | 300 | 600 |
| WkshpSS | 300 | 500 |
| Auditoria | 200 | 300 |
| Lecture | 200 | 300 |
| Office | 300 | 400 |
| Changing | 100 | 100 |
| Circulation | 100 | 100 |
| DrySptHall | 300 | 300 |
| FoodPrep | 500 | 500 |
| Laund | 300 | 300 |
| Plant | 200 | 200 |
| Swim | 300 | 300 |
| Toilet | 200 | 200 |
| EatDrink | 200 | 150 |
| IceRink | 300 | 200 |
| FitGym | 300 | 150 |
| FitStud | 300 | 150 |
| Store | 100 | 50 |
Industrial
| Activity | 2021 | 2013 |
| WareStore | 100 | 300 |
| Reception | 100 | 200 |
| IndProcess | 200 | 300 |
| Office | 300 | 400 |
| Circulation | 100 | 100 |
| FoodPrep | 500 | 500 |
| Plant | 200 | 200 |
| Toilet | 200 | 200 |
| EatDrink | 200 | 150 |
| Lab | 500 | 300 |
| Store | 100 | 50 |
Car Parks 24 hrs
| Activity | 2021 | 2013 |
| Car Park | 75 | 100 |
| Office | 300 | 400 |
| Circulation | 100 | 100 |
| Plant | 200 | 200 |
| Toilet | 200 | 200 |
Universities and colleges
| Activity | 2021 | 2013 |
| Toilet | 100 | 200 |
| Lab | 500 | 800 |
| Offices | 300 | 400 |
| Changing | 100 | 100 |
| Circulation | 100 | 100 |
| DrySptHall | 300 | 300 |
| FoodPrep | 500 | 500 |
| Class Room | 300 | 300 |
| HighDensIT | 300 | 300 |
| Laund | 300 | 300 |
| Lecture | 300 | 300 |
| Plant | 200 | 200 |
| Swim | 300 | 300 |
| Tea | 200 | 200 |
| WkshpSS | 500 | 500 |
| Bed | 100 | 80 |
| Bath | 200 | 150 |
| Communal Area | 200 | 150 |
| EatDrink | 200 | 150 |
| Reception | 300 | 200 |
| FitGym | 300 | 150 |
| Store | 100 | 50 |
Emergency services
| Activity | 2021 | 2013 |
| Reception | 100 | 200 |
| Office | 300 | 400 |
| Cell | 100 | 100 |
| Changing | 100 | 100 |
| Circulation | 100 | 100 |
| DrySptHall | 300 | 300 |
| FoodPrep | 500 | 500 |
| Plant | 200 | 200 |
| Toilet | 200 | 200 |
| Bed | 100 | 80 |
| Bath | 200 | 150 |
| EatDrink | 200 | 150 |
| FitGym | 300 | 150 |
| Store | 100 | 50 |
Residential spaces
| Activity | 2021 | 2013 |
| DomDining | 50 | 150 |
| DomLounge | 50 | 150 |
| DomKitchen | 150 | 300 |
| DomBath | 150 | 150 |
| DomBed | 100 | 100 |
| DomCirculation | 100 | 100 |
| DomCommonAreas | 100 | 100 |
| DomToilet | 100 | 100 |
Passenger terminals
| Activity | 2021 | 2013 |
| Office | 300 | 400 |
| Circulation | 100 | 100 |
| FoodPrep | 500 | 500 |
| Plant | 200 | 200 |
| Reception | 200 | 200 |
| Toilet | 200 | 200 |
| WaitRm | 200 | 200 |
| EatDrink | 200 | 150 |
| Store | 100 | 50 |
Secure Residential Institutions
| Activity | 2021 | 2013 |
| Reception | 100 | 200 |
| WkshpSS | 300 | 500 |
| Lecture | 200 | 300 |
| Offices | 300 | 400 |
| Cell | 100 | 100 |
| Changing | 100 | 100 |
| Circulation | 100 | 100 |
| ClassRm | 300 | 300 |
| DrySptHall | 300 | 300 |
| FoodPrep | 500 | 500 |
| Laund | 300 | 300 |
| Plant | 200 | 200 |
| Toilet | 200 | 200 |
| Bath | 200 | 150 |
| EatDrink | 200 | 150 |
| FitGym | 300 | 150 |
| Store | 100 | 50 |
Crown and County Courts
| Activity | 2021 | 2013 |
| Reception | 100 | 200 |
| Lecture | 200 | 300 |
| Offices | 300 | 400 |
| Cell | 100 | 100 |
| Circulation | 100 | 100 |
| FoodPrep | 500 | 500 |
| Plant | 200 | 200 |
| Toilet | 200 | 200 |
| EatDrink | 200 | 150 |
| Store | 100 | 50 |
Stand alone utility block
| Activity | 2021 | 2013 |
| Changing (all types) | 100 | 100 |
Miscellaneous 24hr activities
| Activity | 2021 | 2013 |
| 24x7Office | 300 | 400 |
| Circulation | 100 | 100 |
| Toilet | 200 | 200 |
| DataCentre | 500 | 500 |
| Heavy Plant Room | 100 | 100 |
| ServerRoom | 100 | 100 |