BRUKL Ventilation Reporting (SBEM v6)
The BRUKL Report has 9 categories (A-I) for classifying local mechanical ventilation:

However, SBEM is not set up to enable all categories to be reported.
The BRUKL Report includes a description of the categories and a separate table listing the zones that have been matched to a category.

Unfortunately there are limitations to what SBEM can report.
This table will only report settings made on the HVAC tab & under the Ventilation Header:

1. Settings made under the Local Ventilation sub-header

Will be classified as B-Zonal supply system where the fan is remote from the zone
If there is also heat recovery

It will be classified as D-supply and extract ventilation units serving a single room or zone with heating and heat recovery
2. Settings made under the header Local Mechanical Extract (also referred to as Exhaust):
Note that Local Mechanical Extract represents a supplementary ventilation system, usually where there are additional contaminants (eg odours from toilets / cooking etc).

1-Fan remote from zone will be reported in C: Zonal extract system where the fan is remote from the zone
2-Fan within zone will be reported in A: Local supply or extract ventilation units serving a single area
3-Fan remote from zone with grease filter will be reported in I: Zonal extract system where the fan is remote the from zone with grease filter
3. Settings made under the 'Do you know the TU specific fan power' header

Note this header only appears if the HVAC System assigned to the zone is either
A Fan Coil Unit OR an Indoor packaged cabinet (VAV)
Terminal Unit SFP will be classified as H: Fan coil units
Thus the following categories are not available to any SBEM v6.1.e interface:
E: Local supply and extract ventilation system serving a single room or zone with heating and heat recovery
F: Other local ventilation units
G: Fan assisted terminal variable air volume (VAV) units
E is not available, perhaps because it is a close duplication of D-supply and extract ventilation units serving a single room or zone with heating and heat recovery. Certainly SBEM has no mechanism to categorise these separately. Additionally, SBEM does not require main ventilation systems to be defined as:
· Supply only
· Extract only
· Supply and Extract
And thus may class systems incorrectly
F is not available as there are only fixed categories of ventilation available
G is not available, presumably due to a bug or software not able to link the zone level input of terminal unit with the system type.
If you have systems which employ any of these missing classifications then you will presumably need to report these on the BRUKL_2 form (model_brukl_2.pdf in the SBEM folder).
DSM
DSM largely has the same issues as SBEM as it was assumed the reporting should follow that used by SBEM. There is one difference however in that DSM can report category G.
Improvements to the reporting in DSM are planned for the v8 release.