Display Lighting on BRUKL
Posted by Andrew Bairstow on 29-Jul-22 04:15 PM
|
|
Part LA 2021 sets out the requirements for Display Lighting in New Buildings:![]() i. have an average light source efficacy of 80 light source lumens per circuit watt
![]() ii. have a rated power usage no greater than 0.3W/m² in each space
iii. the LENI method
![]() Only ONE route to Compliance is required and only i can be demonstrated in SBEM Note that any SBEM Compliance calculation with SBEM v6.1.b or 6.1.c will display options i and ii. Although SBEM does calculate the W/m² this is based on the Display W/m2 set for the Activity in the NCM Activity database so the status of this value (red/black) can safely be ignored. ![]() | |
|