Low Flow showers

Modified on Wed, 3 Sep, 2025 at 5:44 PM

Related Articles:

Activity settings for hot water in SBEM v6

Modelling individual zones to find optimum improvements


Specifying Low Flow showers in the SBEM DHW dialogue can reduce the demand for a DHW system by up to 35%. However, in many cases, low-flow showers and showers employing Waste Water Heat Recovery may not reduce the demand at all.


The SBEM database includes a field representing the Shower Fraction for an Activity (the proportion of hot water demand that is served by showers). This can take a value as high as 0.88 (ie 88% of hot water demand is from showers) or as low as zero. For the majority of activities, the value is zero.


'Low Flow showers' are assumed to have a demand that is 60% that of a 'standard shower' (saving 40%). So when the shower fraction is 0.88, assigning all showers to be low flow will reduce the hot water demand by 40 * 0.88 (35%).

 
A DHW System will likely serve multiple types of activity so a saving as high as 35% would be unusual, however, activities with a high shower fraction also have a very high demand for hot water so a value close to this is feasible.

Note: that all activities with a shower fraction of 0.88 are 'Changing Room with Showers' activities. All these have an exceptional DHW demand that often skews a BRUKL or EPC calculation. Employing low-flow technology in such buildings may well significantly reduce ratings / BER.

Most activities have a shower fraction of zero so won't benefit from specifying low flow showers. However, there are other activities with a non zero shower fraction (0.7 or 0.12). These are listed below:


The following activities have a shower fraction of 0.7. DHW systems supplying these could have a reduced demand of 28% with all low flow showers.



The following activities have a shower fraction of 0.12. DHW systems supplying these could have a reduced demand of 5% with only low-flow showers. 