Ground floor U-values used in constructions adjacent to ground can either be entered as being corrected for 3-D conduction effects or not:

In medium & large buildings the ground acts as a significant heat store, reducing heat losses and the effective U value.
For uncorrected ground floor U-values (for example those calculated by DesignBuilder using the Layers Definition method and based on BS EN ISO 6946) SBEM automatically corrects the U-value based on the floor area of the building and the external wall perimeter length using the equations in BS EN ISO 13370. This 'corrected' U-Value is used in the calculation and reported on the BRUKL.
If you have been provided with U-Values from a professional body, check if these have been corrected and if so make sure the box is ticked.
Reporting differences in SBEM and DSM

SBEM calculates the adjusted U-values for the individual zones
For a building 9m x 6m (all exposed perimeter) with unadjusted U-Value 0.25.
The adjusted U-Values for corner zones (Perimeter/Area = 6/9) are 0.19. For zones with one edge exposed (Perimeter/Area = 3/9) the U-Values are calculated as 0.16. The area weighted average U-Value for the whole block is 0.18:

DSM calculates the adjusted U-Value for the whole block
Thus it uses a Perimeter/Area for the whole block of 30/54 which generates a U-Value of 0.18. This is also the reported maximum U-Value as only one calculation is performed: